I have a situation of 2 sets of 4/0 aluminum in 1 conduit.My calculation was max amps after derate is 328.Could i use a 350 mdp breaker ?
Jim W in Tampa said:We been called down on this before.I am looking at 90 degree colum and geting 205 for 4/0 time 2 = 410 then drerating at 80% for 4-6 conductors and getting 328.The calculated load would be a joke at this point because we dont even have a tenant.
websparky said:Jim,
It looks right to me. Just show them 240.4(B) and 240.6.![]()
iwire said:If you can not produce a calculated load how was the size chosen?
If you can not produce a calculated load maybe the inspector will require protection at 328 or less.![]()
BTW what type insulation and is it in a wet location?
Shhhhh.Often we change things to please ourself and get our own engineer to stamp it.Customers often wave the original for cheaper price on what we suggest.Not saying its right but thats how it goes here.mpd said:jim w
does the engineer know his or her design was changed?
Jim W in Tampa said:I have a situation of 2 sets of 4/0 aluminum in 1 conduit. My calculation was max amps after derate is 328. Could i use a 350 mdp breaker?
iwire said:BTW what type insulation and is it in a wet location?
Jim W in Tampa said:xhhw
Jim W in Tampa said:My calculation was max amps after derate is 328.
Jim W in Tampa said:Could i use a 350 mdp breaker?
Jim W in Tampa said:It is wet and is xhhw-2
iwire said:So 328 amps it is, just as you thought.
So a 350 OCPD could be used.
Why not run two sets of 300 AL in the same raceway for a true 400 amp service?