Hi,
My question is regarding 240.21 b application to tap in following scenario:
I have a 2000Amp service switch fused at 2000amps. The service switch feeds a switchboard rated for 2000amps.
1. If tap after the service switch ( on buss of the switchboard or on the load side of switch), the feeder shall be follow the tap rules. 1/10 of the ampacity of switchboard and the length restriction of 10'.
2. If tap is before the service switch ( on load side of the service switch or inside the C/T), what rule shall the feeder sizing follow? the service feeder (based on OCP) or tap feeder as i am tapping the service switch?
Thanks