phil laxague
Member
- Location
- seattle
our utility service is replaceing our 120/208v, 4 wire service transformer and installing a 480/277v' 4 wire 3 phase transformer. they are using the existing (2) parrallel 700 kcmil. the wires are going to a CT can. I will be going from the CT can to a fused disconnect then to a 600a breaker on a main distrabution panel. i was informed to go with (2) parrallel runs of (4)500 kcmil AL. and 1/0 ground. it seems to me that wire is incorrect. since we have to adjust for 4 current carrying condutors. i also was informed that for service feeders, you don't have to adjust for more than 3 wires. I feel that 400 kcmil CU would do the job! I need some assistance on this. Thanks, Phil.