The GEC only has to be continuous to one item of the GES, bonding jumpers can be used to connect all the other available parts together.Originally posted by mdshunk:
IF the GEC went from the panel to the water pipe and ended in a clamp...
THEN the GEC started at the water pipe with another clamp and went to the ground rod...
THEN you would have a violation. The GEC to the rod would be using an inch or two of the water pipe as the grounding electrode conductor.
On the other hand...
If the GEC passed straight through one clamp at the water pipe and continued straight on to the rod, then you'd be compliant.
Originally posted by electricmanscott:
Roger I am not a what if guy but flying frogs would be cool.
Roger
I don't disagree that it is no big deal but I thought the point of this forum was to argue every little nuance of the code into oblivion.Originally posted by georgestolz:
What if in the future four inches of copper piping were used to connect two pieces of GEC? Oh, the humanity!
Originally posted by electricmanscott:
... but I thought the point of this forum was to argue every little nuance of the code into oblivion.
250.52(A)(1)Originally posted by macmikeman:
Posted by Dillon3c " *exeption - would not apply bieng of residential installation"
Dillon, in what part of 250.52 does it exempt residential?