Service GFCI protection

Status
Not open for further replies.

ksmith846

Senior Member
Quick question......

3000 Amp 120/208 Volt Service does not require GFCI protection per NEC 230.95

Doesn't this Article only pertain typically to 277/480 Volt Services??

Thanks in advance to all
 

mcclary's electrical

Senior Member
Location
VA
Quick question......

3000 Amp 120/208 Volt Service does not require GFCI protection per NEC 230.95

Doesn't this Article only pertain typically to 277/480 Volt Services??

Thanks in advance to all

Are you under one of the five exemptions? Why do you say it is not required?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Quick question......

3000 Amp 120/208 Volt Service does not require GFCI protection per NEC 230.95

Doesn't this Article only pertain typically to 277/480 Volt Services??

Thanks in advance to all
First off they are talking about GFP (ground fault protection) for equipment, not GFCI for personnel. There is a difference.

Secondly, it applies to wye services with more 150 volt to ground.... Your 3 phase 3000 amp 120/208 service is not greater than 150 volts to ground so it is not needed.
 

ksmith846

Senior Member
First off they are talking about GFP (ground fault protection) for equipment, not GFCI for personnel. There is a difference.

Secondly, it applies to wye services with more 150 volt to ground.... Your 3 phase 3000 amp 120/208 service is not greater than 150 volts to ground so it is not needed.

Thanks that is the answer to the question I was trying to ask.
 