Re: Service GFI Testing
Mike:
On new services and as part of maintenance we test GF systems for current pick up at all factory presets for current. The second test is a timed opening of the switch, this test is performed at 150% of the GF relay current setting (hopefully obtained from a coordination study) and the operation of the switch is timed utilizing a function of the test set. Additionally we ducter/microhm/DLRO the power contacts for contact resistance and lastly the service is meggered (watch for controls during this test), line to load with the switch opened, pole to pole and pole to ground with the switch closed and the neutral/grounded conductor disconnect link is removed and the load neutral is meggered to the line neutral.
If there are additional features such as Low voltage relays, phase loss relays or Blown Fuse Trip these features are also tested for proper operation (pick up drop out ect).