There seems to be more than one way to terminate Service Ground wires. If I were to look through Article 250 of the 2002 NEC, there are several sets of illustrations that show the termination of service ground conductors at the Neutral bus. Then there is a bonding jumper run to an equipment grounding bus. At this ground bus they then show the Main bonding jumper to the cabinet enclosure.
This is all fine for a residential or small commercial service but what about a larger service such 1000 or 2000 amps? For something this large I would expect all service grounding conductors to be terminated on the ground bus, and then a ?bonding jumper? from the ground bus to the neutral bus. In the case of some Ground Fault Protection Systems, this bonding jumper is where the current transformer is installed so as to monitor against current flow through the grounding conductors.
Is there an inconsistency in how the NEC shows the Ground Conductors connections?
This is all fine for a residential or small commercial service but what about a larger service such 1000 or 2000 amps? For something this large I would expect all service grounding conductors to be terminated on the ground bus, and then a ?bonding jumper? from the ground bus to the neutral bus. In the case of some Ground Fault Protection Systems, this bonding jumper is where the current transformer is installed so as to monitor against current flow through the grounding conductors.
Is there an inconsistency in how the NEC shows the Ground Conductors connections?