Wouldn't the grounding in this be a violation? I could understand one or the other at the CT or at the MDP.
recthree said:you would not have the ground rod comming out of the meter base,it is considered not accessable. .
recthree said:you would not have the ground rod comming out of the meter base,it is considered not accessable.
M. D. said:Who said anything about ground rods???
SmithBuilt said:
Wouldn't the grounding in this be a violation? I could understand one or the other at the CT or at the MDP.
cadpoint said:the MDP should be labeled "SE",
SmithBuilt said:I don't think there will be any building steel, well probably a concrete encased electrode. Of course incoming waterline.
If I tied the 3/0 from the mdp to the rebar and water line. Wouldn't another grounding electrode at the ct create a parallel path, along with the service neutral conductor?
In this drawing, it's saying "3/0 conductor in a 3/4" conduit", right?iwire said:My mistake, I took the "3/0- 3/4" as a 3/0 to a 3/4" rod.
A parallel path through what? The earth only? If that what you're saying, that's perfectly compliant.SmithBuilt said:If I tied the 3/0 from the mdp to the rebar and water line. Wouldn't another grounding electrode at the ct create a parallel path, along with the neutral conductor?
iwire said:It could be called "Cadpoint" there is no requirement to call the panel SE.
cadpoint said:230.66 ...
georgestolz said:In this drawing, it's saying "3/0 conductor in a 3/4" conduit", right?
A parallel path through what? The earth only? If that what you're saying, that's perfectly compliant.