I had asked this in an earlier string but the discussion went off track a bit.
I have a customer owned pad mounted transformer (1500kVA) providing a 480V "service" to a hospital. i.e. hospital is primary metered. Since the utility does not own the transformer, may this still be called a service transformer.
If I am to treat it as one, I would run a service grounded conductor in lieu of a neutral and a ground correct?
And if this is a service, I may take advantage of 230.90 which permits me to protect these secondary conductors with a device which is in series with them. i.e. in this case the main breaker inside the building in the main switchboard. Are we in agreement so far?
If this is not a service transformer because it's owned by the customer, then I'd need to provide a neural and a ground on the secondary and my protective device on the secondary side would have to be no more than 25 feet from the transformer correct?
I really appreciate your collective help on this!
Thanks,
Mike
I have a customer owned pad mounted transformer (1500kVA) providing a 480V "service" to a hospital. i.e. hospital is primary metered. Since the utility does not own the transformer, may this still be called a service transformer.
If I am to treat it as one, I would run a service grounded conductor in lieu of a neutral and a ground correct?
And if this is a service, I may take advantage of 230.90 which permits me to protect these secondary conductors with a device which is in series with them. i.e. in this case the main breaker inside the building in the main switchboard. Are we in agreement so far?
If this is not a service transformer because it's owned by the customer, then I'd need to provide a neural and a ground on the secondary and my protective device on the secondary side would have to be no more than 25 feet from the transformer correct?
I really appreciate your collective help on this!
Thanks,
Mike