lvdugger
Member
- Location
- owensboro kentucky
INSTALLATION. THE LOCAL UTILITY REQUIRES YOU TO HAVE A CUSTOMER OWNED 13800 VOLT SERVICE POLE WITH ISOLATION SWITCH AND FUSEABLE CUTOUTS. YOU ARE FEEDING A 3000 KVA 13800 VOLT DELTA TO A 480/277 VOLT WYE OUTDOOR TRANSFORMER . FEEDING FROM TRANSFORMER TO A 3000 AMP 480/277 VOLT MAIN SWITCHGEAR IN A BUILDING. WHERE IS THE MAIN SERVICE DISCONNECT? THE SERVICE POLE OR THE MAIN IN THE BUILDING? CAN YOU PULL 3 PHASES AND A NETURAL AND BOND THE NEUTRAL IN THE TRANSFORMER AND BOND THE NETURAL AT THE 3000 AMP MAIN SWITCHGEAR ? OR DO YOU HAVE TO PULL NETURALS AND GROUNDS FROM THE TRANSFORMER TO THE SWITCHGEAR AND TREAT SWITCHGEAR AS A SUB PANEL. THANKS