Service Grounding at Fire Station

Status
Not open for further replies.

j2020

Member
Location
California
Occupation
Engineer
I'm working a on fire station project that was built in 1977. We are replacing two existing panels (Panel "P" and Panel "L"). Based on the attached one line diagram the grounding it at the service pullbox but appears there are no ground wires going to the panelboards we are replacing. Would I need to run new ground wires from the service pullbox ground to each panel we are replacing to meet current NEC 250 grounding requirements?
 

Attachments

  • capture.pdf
    182.4 KB · Views: 11
Since you have OCP at the gutter ahead of the Panels there would need to be an equipment ground however that ground could be a properly installed meratllic raceway and not necessarily a separate wire conductor.
 