Andy Sherrill
Member
I have a baseball field lighting application where I have an existing pad mount transformer supplying single phase 120/240 V. The project I have is to add a DP near the transformer to supply lighting to 3 fields. There is already one dp at one of the fields and another service disconnect on the concession building. As I understand, code requires a ground at the new service disconnect (DP), and the ground must connect to the grounded conductor. The new DP will be located close to the transformer and it's ground rod(s) or possible grid. If I drive a ground rod at the new DP, this ground rod could end up very close to the existing grounds for the transformer. With the neutral connected to the ground rod at the new DP and connected to the transformer grounds, it seems to me that I could be creating a parallel path for neutral current under certain soil conditions. I understand the earth is not a great conductor, but in close proximity it seems I could have neutral current flow on the "ground" system. Does anyone have any experience with this? Is it allowed to treat this like a feeder and install a four wire service with a full size equipment ground? I am concerned for safety, but also because the lighting control system is electronic, so any objectionable ground currents will cause problems. Thanks in advance for anyone who has thoughts or experience that might help!