Service Grounding Location
Is it National Electrical Code 2014 compliant if the grounding electrode conductor is run up the outside of a building and connected to the grounded service conductor, on the load end of the service point, where it was spliced to the utilities service drop?
Do you know if this Utility allows this method of service grounding?
(This service grounding single location only option seems to be suggested both by the 2011 NEC Handbook Section 250.24 on page 219 and in the Soares Book on Grounding and Bonding Ninth Edition page 67.)
Is it required that an additional connection of the grounding electrode conductor be made to the grounded service conductor at the service disconnecting means?
It seems to me that the premise electrical system would be effectively grounded using only the one connection at the service point. In some instances this could be a more practical installation.
In addition, the electrical equipment grounding could be made in the service disconnecting means by the use of a main bonding jumper from grounded service conductor to service enclosure.
Thanks
Is it National Electrical Code 2014 compliant if the grounding electrode conductor is run up the outside of a building and connected to the grounded service conductor, on the load end of the service point, where it was spliced to the utilities service drop?
Do you know if this Utility allows this method of service grounding?
(This service grounding single location only option seems to be suggested both by the 2011 NEC Handbook Section 250.24 on page 219 and in the Soares Book on Grounding and Bonding Ninth Edition page 67.)
Is it required that an additional connection of the grounding electrode conductor be made to the grounded service conductor at the service disconnecting means?
It seems to me that the premise electrical system would be effectively grounded using only the one connection at the service point. In some instances this could be a more practical installation.
In addition, the electrical equipment grounding could be made in the service disconnecting means by the use of a main bonding jumper from grounded service conductor to service enclosure.
Thanks