delaware74b
Member
- Location
- Delaware, USA
I am the process of installing new service equipment on 2 apartment buildings. Each building will have a 1000-amp main breaker feeding approximately 15 meters on a sq-d ez stack. Incoming feed is 120/240 single phase with 3 sets of parallel 500 AL xhhw. #6 bare to 2 ground rods 6 feet apart. I am also running a bond wire to the 2" copper water line where I comes into the building. My question is the #2 copper (or 1/0 AL) the proper size, based on NEC 250.66? I will also have to bond the gas line in one building. That boiler provides all domestic hot water and baseboard heat in both buildings. Do I use the same #2 size for the gas line or is it 2/0 cu based on 250.122? The boiler room has its own 100 amp subpanel coming off a 225 amp panel next to the meter stack.
These apartments are from the 1950's with original panels and wiring that has been not touched. Panels are being replaced after the new main gear is turned on.
These apartments are from the 1950's with original panels and wiring that has been not touched. Panels are being replaced after the new main gear is turned on.