I have a situation where a service for a property comes in to shed type structure, the office and actual place where the business is being done is a separate structure from said shed
The water main for the building comes in to the office not the shed
My question is if we run a feeder from the service , bond the neutral at the service like we should and install an isolated neutral at the office structure with it's on GES do we just drive two grounds rod at the service and be done
My thoughts are that the metallic water system needs to also be bonded to the GES and the separate structure.
I could not find anything in the code book about this besides the fact that all electrodes need to be bonded
Thoughts?
Sent from my SM-G986U using Tapatalk
The water main for the building comes in to the office not the shed
My question is if we run a feeder from the service , bond the neutral at the service like we should and install an isolated neutral at the office structure with it's on GES do we just drive two grounds rod at the service and be done
My thoughts are that the metallic water system needs to also be bonded to the GES and the separate structure.
I could not find anything in the code book about this besides the fact that all electrodes need to be bonded
Thoughts?