Service Grounding

Status
Not open for further replies.

dvcraven0522

Member
Location
St. Louis, Missouri
Occupation
Engineer
I have been asked to provide a grounding detail for (2) services. See attached PDF. I appreciate any comment!

Thanks
Dan Craven
 

Attachments

  • 6B ELECTRICAL BW Case-E0.0.pdf
    66.7 KB · Views: 24
The GEC's to the water pipe are too small. Since you have a CEE ground rods are not required. Also the #3 aluminum on the secondary of the transformer are too small for a 100 amp OCPD.
 