Yes, assuming that the 400 amp fused disconnect is not at the building.See attached image, can we have the service grounding (bond to ground rod, metallic water pipe, ufer, etc.) at panel DPA but not at the 400A fused disconnect after utility transformer?
That is correct. I assumed there would be a grounding electrode system at the remote disconnect. I need to learn to read the questionIs that 200' between the service disconnect at the transformer and the DPA underground? If so then you'll need a GES at each location.
Yea, 400A fused disc by the xfmr, main panel us 200 feet away at the building and underground feeder. Thought the code only allows GES at first disconnect after service transformer?Yes, assuming that the 400 amp fused disconnect is not at the building.
No a GES is required at each separate structure. Since you have a feeder to the building the GEC would terminate at the EGC bus not on the neutral bus. Take look at 250.32.Yea, 400A fused disc by the xfmr, main panel us 200 feet away at the building and underground feeder. Thought the code only allows GES at first disconnect after service transformer?
Yea, 400A fused disc by the xfmr, main panel is 200 feet away at the building and underground feeder. Thought the code only allows GES at first disconnect after service transformer?
Yes. The service conductors end at the 400 amp service disconnect so anything down stream of that cannot have the neutral and EGC connected together therefore you would connect the GEC at the building to the EGC bus. The neutral bus would not be bonded at the building.What you said … GES is required at both locations but ground and neutral bond can only be established at the 400A fused disc, correct?
I assume you know that you will need an egc from the remote disco to the MDPGot it. TY
Just curious does your utility require the disconnect the one out near what you identified as a utility transformer.Yea, 400A fused disc by the xfmr, main panel us 200 feet away at the building and underground feeder. Thought the code only allows GES at first disconnect after service transformer?
480V/277V service, yes the client needs a main service fused disconnect within sight of the poco xfmr secondary or the underground service feeder needs to be concrete encased.Just curious does your utility require the disconnect the one out near what you identified as a utility transformer.
Also curious as to what voltage the 400 amp service is.
Also curious as to the location of the meter
: here the utility would only run there conductors 100 ft onto the customer's premises if it was a service drop.
: the utility here would not have that same restriction on a utility lateral.
Also for certain voltages for line voltage metering the utility will require a site isolation switch that is not a service disconnect.
I ask because if something like that is going on it might change some of the answers given.
Over the years I have learned to answer questions that I receive over the phone with a prefix.
If I am understanding what you are seeing than this is your answer
Kind of the reason I ask the questions.480V/277V service, yes the client needs a main service fused disconnect within sight of the poco xfmr secondary or the underground service feeder needs to be concrete encased.
i think that needs clarification. Is it a service disconnect or not480V/277V service, yes the client needs a main service fused disconnect within sight of the poco xfmr secondary
That sounds like a utility regulation. If so than that portion would be part of the utility lateral.or the underground service feeder needs to be concrete encased.
I should have said is the main bonding jumper required by the NEC at the fused disconnect or at the buildingHere the isolation switch would be required to have a grounding electrode by utility regulations.
The big difference, is a equipment ground required from the fuse disconnect to the building or not.
Is the main bonding jumper
the NEC requires it at the service location. The utility regulations here would require a neutral bonded grounding electrode at the isolation switch. We wouldn't call what the utility requires a main bonding jumper.required at the fused disconnect or at the building