Service Grounding

Status
Not open for further replies.

Irishelectric

New member
I am working on an old commercial building, it has a 200amp meter main its single phase 240v 3 wire. from the meter main to the panel there are only 3 wires, can i drive a ground rod at the panel or am i required to pull a ground wire from the meter main to the panel.
 
You need an equipment grounding conductor between the main and the panel. The grounding electrode conductor must be connected at the main. Note, a metal raceway can serve as the required equipment grounding conductor.
 