W wireperson Senior Member Location Florida Dec 6, 2008 #1 does it need to be a bare conductor or it can be insulated , prints call for a #2 thwn , its a 400 A service
does it need to be a bare conductor or it can be insulated , prints call for a #2 thwn , its a 400 A service
Rockyd Senior Member Location Nevada Occupation Retired after 40 years as an electrician. Dec 6, 2008 #2 250.119 and 250.119(A) Bare is probably cheaper, but if six or larger, re-identify.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Dec 6, 2008 #3 What size are the service entrance conductors? #2 sounds small. It could be bare or insulated and is not required to be green.
What size are the service entrance conductors? #2 sounds small. It could be bare or insulated and is not required to be green.