A metal service gutter feeding 2 disconnects with pvc nipples with two sets of service conductors 3/0 from meter. What is the best way to bond the gutter?
Perhaps a lay in lug (2 in this case) would be cheapest and easiest?Some type of lug that can be used to connect the neutrals to the gutter.
I usually use this method. Only slight hiccup is NEC doesn't address SSBJ's for services with multiple enclosures. Sizing for each enclosure like s GEC tap seems logical, but is not stated.Probably the easiest way would be to use a #4 from each disco neutral bar back to a 2 hole lug bolted to the gutter.
Can a polaris be used for both neutrals and come off the polaris tap to gutterSome type of lug that can be used to connect the neutrals to the gutter.
Could be, a bare set of terminals mounted directly to the enclosure would also work.Can a polaris be used for both neutrals and come off the polaris tap to gutter
That's what I was thinking of.Used to use stud bolt kerneys.
Neuitral insulation is removed but conductor is not cut. Eliminates a potential loose connection.
View attachment 2555597
I haven't seen one of those, but I have seen regular split bolts used the same way with the right-sized hole.Used to use stud bolt kerneys.
Neuitral insulation is removed but conductor is not cut. Eliminates a potential loose connection.
View attachment 2555597