service gutter bonding

Status
Not open for further replies.

Seekthetruth

Member
Location
Florida
Occupation
Electrical
A metal service gutter feeding 2 disconnects with pvc nipples with two sets of service conductors 3/0 from meter. What is the best way to bond the gutter?
 
Some type of lug that can be used to connect the neutrals to the gutter.
 
Some type of lug that can be used to connect the neutrals to the gutter.
Perhaps a lay in lug (2 in this case) would be cheapest and easiest?
Probably the easiest way would be to use a #4 from each disco neutral bar back to a 2 hole lug bolted to the gutter.
I usually use this method. Only slight hiccup is NEC doesn't address SSBJ's for services with multiple enclosures. Sizing for each enclosure like s GEC tap seems logical, but is not stated.
 
You could even connect each end of a wire to one neutral conductor, and land the middle of it in a single lug.
 
Used to use stud bolt kerneys.
Neuitral insulation is removed but conductor is not cut. Eliminates a potential loose connection.
1614797040884.png
 