Jerseydaze said:
Two Questions I'm Bidding on a 200 amp underground service in New Jersey the Service is Approx 75 feet from the pole I am bidding around $3500 am I in the ball park?
A typical OH service (SE) from me is at $2600.
Last OH service I did with pipe was at $2835 (200A, 20' EMT, etc)
Just the 2/0 wire alone there (COG) is about $458 ...adding your markup, handeling/pulling, etc... that would easily be $1000.
You might be "in the park"...but what type wire/conduit are you planning on?
PVC and wire?
Direct burial?
Money for temp service?
Jerseydaze said:
Question 2 As far as I can tell my minimum burial depth is 18 inches I cant remember doing a UG service for my old bosses that was less then 3' down whats the rule also I always remember my bosses ordering sand is this required . Any advise on this is greatly appreciated
Burial depths are in 300.5
The lateral may be covered under your POCO's "green book".
For me, that would be PSE&G.
Here is some of what they have to say:
NOTE: #9 above details the sand issue
http://www.pseg.com/customer/business/new_service/pdf/RequirementsElecSvc2005.pdf
You can get better images right from the PSE&G "green book" (in .pdf format ~ you'll need an Adobe Reader ~ if you don't have one already, it's free at
www.Adobe.com)