I have an existing overhead service with parallel 3 inch risers with 4 - 500 KCMIL thhn stranded copper conductors with rack mounted ct's at weatherheads . Just inside building is service gutter with two 400 amp 480 volt 3 phase disconnects tapping parallel service. Customer wants to replace overhead with underground lateral. I was planning to set ct can on backside of gutter running 2 - 3 inch pvc conduits underground and up transformer pole on stand off brackets.
1. Is the existing installation legally sized for 800 amp service taking into consideration the 75 degree / 90 degree ampacity ratings and for termination rating.??
2. Considering I will be using schedule 80 pvc for vertical runs is the conduit fill legal for 4- 500 kcmil ?
1. Is the existing installation legally sized for 800 amp service taking into consideration the 75 degree / 90 degree ampacity ratings and for termination rating.??
2. Considering I will be using schedule 80 pvc for vertical runs is the conduit fill legal for 4- 500 kcmil ?