A service lateral enters a 320 meterbase (no disconnect) on a single family dwelling. SE conductors run from the meterbase to a service disconnect on the opposite interior wall.

The service lateral now exits the meterbase twice (using proper lugs), each feeding an outbuilding. Now we have a total of three structures. All conductors are properly sized.

Is this a violation of 230.40 exc. 3?
 
The way I read the exception you can only go to one separate structure. IMO you'll need three disconnects grouped together.
 
sounds like another Code change is in order.. ....dwelling unit and seperate structure(s)....
 
buck33k said:
I don't know..would'nt each set leaving the meterbase be considered its own service lateral to that building?
Nope, the lateral ends at the meter base.

Service Lateral. The underground service conductors between the street main, including any risers at a pole or other structure or from transformers, and the first point of connection to the service-entrance conductors in a terminal box or meter or other enclosure, inside or outside the building wall. Where there is no terminal box, meter, or other enclosure, the point of connection is considered to be the point of entrance of the service conductors into the building.
 
buck33k said:
I see...Say there were only two structures. What would you call the conductors running from the meterbase to the outbuilding?
Do you have the NECHB? Exhibit 100.16 shows the difference.

Service-Entrance Conductors, Underground System. The service conductors between the terminals of the service equipment and the point of connection to the service lateral.
FPN: Where service equipment is located outside the building walls, there may be no service-entrance conductors or they may be entirely outside the building.
 
buck33k said:
I see...Say there were only two structures. What would you call the conductors running from the meterbase to the outbuilding?

Are these laterals??? connected to the line side of the meter base or the load side? In other words do the other buildings have a meter also?
 
Service-Entrance Conductors, Underground System. The service conductors between the terminals of the service equipment and the point of connection to the service lateral.
FPN: Where service equipment is located outside the building walls, there may be no service-entrance conductors or they may be entirely outside the building.

Thanks for the reference Chris. I don't have the NECHB. Is The meterbase really service equipment by Art 100 definition? In the example of the conductors to the outbuilding, they are not connected to the terminals of the service equipment.
 
buck33k said:
Connected to the load side of the meter Dennis. No meters on the other structures.
Then I would not call them laterals either but I would call them service entrance conductors.