I've been asked to install a service to supply 24 1500 watt plug in resistance type electric heaters in a rooming house to supplement the baseboard hot water heat in 24 rooms.I am wondering if I can consider them as appliances and use the demand factors in table 220-42 or would I have to assume they would be likely to be used at the same time. I was going to figure 20000w at 50% and 16000 w at 40% giving me 16400w of calculated service load if I used the demand table. That seems pretty low .I am also insralling 4 tankless electric water heaters 14.5 kw each. 14.5kw x 4=58 kwx75%=43.5kw. total calculated load would be 59900w if I don't consider any of above as continuos load.59900w/240v=250 amps.do you think I've figuring service way too low