T triplex15 Member Location Virginia Feb 2, 2009 #1 What is the requirement or code article for installing 200amp 120/240v service disconnects in the same room as a Hot tub. It is a recroom in a residential house with a Hot Tub inside and the service location is about 16 feet away. Thanks
What is the requirement or code article for installing 200amp 120/240v service disconnects in the same room as a Hot tub. It is a recroom in a residential house with a Hot Tub inside and the service location is about 16 feet away. Thanks
D DRGREG Member Location Port Washington, WI, USA, Earth, Etc. Feb 2, 2009 #3 110.26 would be the main concern.
K kjless Member Location plaistow nh Feb 2, 2009 #5 it is 5' but in 680.41 it also says adjacent to and within sight of then says this requirement does not apply to single family dwelling.
it is 5' but in 680.41 it also says adjacent to and within sight of then says this requirement does not apply to single family dwelling.
Jim W in Tampa Senior Member Location Tampa Florida Feb 2, 2009 #6 kjless said: it is 5' but in 680.41 it also says adjacent to and within sight of then says this requirement does not apply to single family dwelling. Click to expand... This is not the disconnect to his spa the way i read it, simply a panel within the same room.
kjless said: it is 5' but in 680.41 it also says adjacent to and within sight of then says this requirement does not apply to single family dwelling. Click to expand... This is not the disconnect to his spa the way i read it, simply a panel within the same room.