Service Mast discussion.

Ryguy604

Member
Location
Vancouver
Occupation
Electrical Inspector
Hello All . appendix B on (6-122 (5) . In the picture below does the min height between he roof and POA need to be 915mm in this scenario. Technically the POA is on the the pipe so therefore its considered a mast. . However my main inquiry here is the 915mm rule as per appendix B. Does the 915 mm rule apply only to when the service conduit is going through the eves trough... I wish I knew how to attached a picture on here or screenshot. It would make alot more sense
I have attached a picture and hoprfully it come up Im new at this .
You can see like 4 non compliances as it from the picture alone.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Hello All . appendix B on (6-122 (5) . In the picture below does the min height between he roof and POA need to be 915mm in this scenario. Technically the POA is on the the pipe so therefore its considered a mast. . However my main inquiry here is the 915mm rule as per appendix B. Does the 915 mm rule apply only to when the service conduit is going through the eves trough... I wish I knew how to attached a picture on here or screenshot. It would make alot more sense
I have attached a picture and hoprfully it come up Im new at this .
You can see like 4 non compliances as it from the picture alone.
List your grievance.
It looks good from here.
Those are not above the roof.
 

Ryguy604

Member
Location
Vancouver
Occupation
Electrical Inspector
-Can use cobra clamps for supporting the mast. Its not a through bolt assembly
-Still trying to find out if the 915mm above the roof line is suppose to be through roof mast or riser side of the building mast. Its to do with snow build I know that.
-the min height for public access is 12 feet AFF and they have 11 cant tell from picture
- They have more than 1.5m of unfused cabling inside as well. 1.5m max termination to termination. Cant tell from picture as well
 