The scope is to upgrade few of the existing risers (from 60A to100Amps), and replace old 60A fusible pullouts with feed-through type 100A /two pole breakers
Meter bank is located in tight electrical closet (on 38th floor) so our only option is to work within the existing enclosure. My question is – if we swap few pullouts with CBs and install custom cover plate –would that pass or we stepping in to issues with UL listing etc.
Pics for the reference
Appreciate your input .
Thank You.