lielec11
Senior Member
- Location
- Charlotte, NC
I am having a discussion with an engineer regarding sizing the incoming service neutral to a service switch for a fire pump. Code dictates you need to run a neutral to the line side of the service switch, even if you do not need the neutral on the load side (i.e. a motor like a FP). Our disagreement stems on what section/table that should be used to size this neutral.
The engineer is pointing to NEC 250.24(C) which refers to "the grounded conductor brought to service equipment.", which then points to Table 250.66 for grounding electrode conductors.
I always thought the purpose to table 250.66 was to size GECs only, and that the service netural was the same size as the phase-conductors.
1) Is this a wrong assumption?
2) Is "grounded conductor" an AKA for a neutral?
I feel like all the neutrals I ever see are the same as the phase wires, not sized by Table 250.66.
The engineer is pointing to NEC 250.24(C) which refers to "the grounded conductor brought to service equipment.", which then points to Table 250.66 for grounding electrode conductors.
I always thought the purpose to table 250.66 was to size GECs only, and that the service netural was the same size as the phase-conductors.
1) Is this a wrong assumption?
2) Is "grounded conductor" an AKA for a neutral?
I feel like all the neutrals I ever see are the same as the phase wires, not sized by Table 250.66.