GingerZap
Member
- Location
- Waller, TX
- Occupation
- Veteran / Electrical Student
I am in an Electrical Program taking an NEC 1 class and my teacher is no help. I am trying to wrap my mind around service neutral loads and am wanting to check my work to make sure I am on the right track. Below is the question and how I solved it. Can anyone verify if my answer is correct?
An eighteen-unit multifamily dwelling contains the following appliances in each unit: a 1-kVA, 115-volt dishwasher; a 1/3 HP, 115-volt in-sink waste disposer; and a 4500-watt, 230-volt water heater. Using the standard method, what is the service neutral load contribution, in volt-amperes, for these appliances? (Assume water heater watt rating equivalent to volt-ampere.)
85,428 Volt-Amperes
Service Neutral Load is the maximum unbalance of the load determined. The maximum unbalanced load shall be the maximum net calculated load between the neutral conductor and any one ungrounded conductor as per 220.61(A). (Is this the Line 10 Calculation?)
Using the Standard Method Load Calculation for Multifamily Dwellings, Line 10 Fastened-In-Place Appliances Rated ¼ hp or 500 Watts or Greater 220.53.
Dishwashers 1000 VA x 18 = 18,000 VA
In-Sink Waste Disposers 1/3 hp (7.2amp) x 115V = 828 VA x 18 = 14,904 VA
Water Heaters 4,500 x 18 = 81,000 VA
18,000 + 14,904 + 81,000 = 113,904 VA (Derate to 75% because there are more than four)
113,904 x .75 = 85,428 Volt-Amperes
An eighteen-unit multifamily dwelling contains the following appliances in each unit: a 1-kVA, 115-volt dishwasher; a 1/3 HP, 115-volt in-sink waste disposer; and a 4500-watt, 230-volt water heater. Using the standard method, what is the service neutral load contribution, in volt-amperes, for these appliances? (Assume water heater watt rating equivalent to volt-ampere.)
85,428 Volt-Amperes
Service Neutral Load is the maximum unbalance of the load determined. The maximum unbalanced load shall be the maximum net calculated load between the neutral conductor and any one ungrounded conductor as per 220.61(A). (Is this the Line 10 Calculation?)
Using the Standard Method Load Calculation for Multifamily Dwellings, Line 10 Fastened-In-Place Appliances Rated ¼ hp or 500 Watts or Greater 220.53.
Dishwashers 1000 VA x 18 = 18,000 VA
In-Sink Waste Disposers 1/3 hp (7.2amp) x 115V = 828 VA x 18 = 14,904 VA
Water Heaters 4,500 x 18 = 81,000 VA
18,000 + 14,904 + 81,000 = 113,904 VA (Derate to 75% because there are more than four)
113,904 x .75 = 85,428 Volt-Amperes