jeff43222
Senior Member
- Location
- Minneapolis, Minnesota
I recently started using SER for services, only to discover that the supply houses don't carry 3-conductor cable where all of the conductors are the same gauge (it's often 2-2-4 or something like that). Usually for services I would use the same size wire for the neutral that I use for the ungrounded conductors, since the neutral must be sized according to the maximum unbalanced load (220.61). Not knowing how balanced the load might be, I always like to play it safe and have the neutral the same size.
If I want to buy SER with all of the conductors the same size, the only stuff they carry also has a ground wire, which I have no use for. But I'm wondering if service neutrals are allowed to be smaller than the ungrounded conductors. Since 220.61 says that "The maximum unbalanced load shall be the maximum net calculated load between the neutral and any one ungrounded conductor.", that alone seems to indicate that the neutral should probably be as big as the ungrounded conductors.
Or am I missing something?
If I want to buy SER with all of the conductors the same size, the only stuff they carry also has a ground wire, which I have no use for. But I'm wondering if service neutrals are allowed to be smaller than the ungrounded conductors. Since 220.61 says that "The maximum unbalanced load shall be the maximum net calculated load between the neutral and any one ungrounded conductor.", that alone seems to indicate that the neutral should probably be as big as the ungrounded conductors.