Can I get some help on an electrical service to a commercial strip center. It is an existing small strip center, with a 1200a 3ph service, 208v, with a tap box fed from underground service. There are 6 existing 100 to 200A services, there is no main. A tennant is wanting to add another meter, and that woud be a total of 7 individual mains, The individual units are divided by firewalls, so are they considered 6 individual buildings? Can a 7th disconnect be added without adding a building main? 230.2 states no more than 6 to a building, but multi occupancy buildings seperated by firewalls are by definition individual buildings. What are your thoughts
Thanks in advance