service over outdoor steps

Status
Not open for further replies.

difowler1

Senior Member
I thought I remembered that the meterbase or the panel box can't be installed over outdoor steps. Or is it just the panel box. I can't find the article.
 
An enclosure with a meter and no overcurrent devices would not be covered by article 240. The panelboard ... lets just say it is the overcurrent devices that are not allowed over the steps in 240.24(F).
 