Service overcurrent protection

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have 200A fused service disconnect fused at 200A. The incoming service conductors are 2/0 awg copper which is good for 175A. Demand load is 171 A.

Should not the fused in the main service disconnect be 175A and not 200A Or 2/0 awg change from 2/0 awg to 3/0 awg copper?


Sent from my iPhone using Tapatalk
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Unless it's residential and meets 310.15(B)(7) or possibly Art 430 Part II
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Who owns the service conductors you are talking about? Are they POCO property?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Which code section actually requires to change 2/0awg to 3/0 awg or 200A fuse to 175A fuse for commercial?
For a dwelling service you can apply the 83% rule to the conductors so 200*83%=166 amps minimum conductor size. #2/0@175 amps is code compliant. Once you go to a commercial service the 83% rule cannot be applied so the 200 amp OCPD would require a 200 amp conductor.
 