Assume a 400A service consisting of 2 - 200A main circuit breaker panelboards. From the service point to the meter socket, parallel 2/0 AWG conductors are used for the ungrounded conductors. On the load side of the meter socket, single 3/0 AWG conductors are installed to each 200A panelboard. The total calculated load is 250A.
Does this arrangement meet all the requirements of the NEC - (230.90, 310.15)?
The paralleled 2/0 AWG conductors will not be loaded to greater than 250A and have a derated ampacity of 280A. This complies with Exception #3 to 230.90(A). However, the individual service entrance conductors to each 200A panelboard must comply with the 310.16 rating of 200A or 3/0 AWG...
(The occupancy is not a dwelling)