danscape said:let's say i have 120/240 V 100 AMP panel
and have single load using 240 V and 50 AMPs......
have i reached 100% of panel rating since both hot wires are loaded with 50 AMPS, or i'm just at 50% ?
infinity said:So in your scenario a 50 amp 240 volt load would use 50% of the capacity of a 100 amp panel.
mull982 said:Is it safe to say that in this example that each leg or pole of the breaker is capable of supporting up to 100A no matter what combination of loads were put on them?
To kingpb's answer, let me add that an amp leaving the panel on one leg does not know whether it will return to the panel on the neutral or on the other leg.mull982 said:Is it safe to say that in this example that each leg or pole of the breaker is capable of supporting up to 100A no matter what combination of loads were put on them?