jagster said:
Can't find code fault with a panel located in an interior wall (2x4), my concern is the ser cable and all the individual circuit feeds going up from the top of the box and the possibility of damage due to lack of depth in a 2x4 wall. Any thought or suggestions...Thanks Joe
The cables have to be protected when they pass thru any framing members if they (the edges of the hole) are less than 1 1/4" from the surface of the member.
As far as protection between the studs, etc, ...they're on their own...not protected.
After the insulation is installed in a 2x4 stud wall, most conductors will be touching the drywall or the outer sheathing on one side or the other of the insulation....really close to the surface. To my knowledge, this is allowed by code (not prohibited).
Most home construction around here is 2x4 wood studs with 7/16 OSB sheathing and NMB wiring. The framers should not use any nails longer than 1 3/4" long to attach the OSB.
A skilled carpenter knows this.
If I'm around when they're framing (usually am a time or two), I check the nail length and "educate" the framers about nail penetration depth and exactly what they might hit (my wiring, plumbing, etc.) if the nails are too long.
Kinda like "a ounce of prevention is worth a pound of cure" type reasoning.
If I have any doubts, I'll walk thru the house and "tug" at the wire where it passes thru the studs, checking for nail penetration.
The thing that bothers me most is a nail gun in the wrong hands.
The carpenter doesn't know (cant tell) whether he's hitting a stud or not.
If he misses the stud, he may run a whole row of nails thru the sheathing and never hit the stud.
Even if he re-nails it, he doesn't pull the missed nails.
If this happens on a stud that has wire stapled to it, you may have 10 or 12 exposed nails that you have to remove or else the cable will be touching them
If you don't pull them, the insulator may push the cable against the nails, and that can create a future problem.
Even if the nail penetrates the wire insulation, it won't always cause a (recognizable) problem.
I'd hazard a guess that it happens pretty regularly and is never known unless it goes between (and makes contact) with a hot and one of the grounds.
With the requirement to use AFCI breakers, it's a big problem if it makes contact with any two of the conductors, and is difficult to find if the drywall is already installed.
As I said, it's worth checking before the drywall.
Just a few thoughts
steve