Does anyone know of any NEC codes relating to mounting a service panel on a ceiling, or overhead? I can see the difficulty involved with working on a panel in this location! but is it against code? Thanks, Bertronix
 

stamcon

Senior Member
Re: service panel mounting

Bertronix, I don't see a section in the 99 NEC that would directly prohibit it. I think it would fall on the manufacturer's installation instructions(listing?) 110-3(b).
 

physis

Senior Member
Re: service panel mounting

I haven't checked the book but it needs to be readily accessable.

[ May 08, 2003, 01:12 AM: Message edited by: physis ]
 

physis

Senior Member
Re: service panel mounting

I'm still a student of the code book but I think these apply 230.70(A), 230.70(1), 230.91.

[ May 08, 2003, 01:15 AM: Message edited by: physis ]
 

dmpaul

Member
Location
Minnesota
Re: service panel mounting

I can't seem to find the code that states that the service disconnecting means must not be taller than 6' in height, but check out 110.26(A)2,3, and (E). If you follow those rules of below 6', nothing extends farther than 6" in front of the panel 6' beyond panel, for the service space to the ceiling or 6' rule. I wouldn't have a problem with it as long their was a reason, then again the ole trusty authority having jurisdiction!! Always an easy cop out huh!! lol
 

davidw

Member
Re: service panel mounting

Bertronix:
It would not be practical or safe to install the panel on the ceiling, but as far as the code, (1) check the mfg's listing on the panel, and (2) look at 2001 cec 380-8(a)for max height of breakers above the floor or working platform. David
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: service panel mounting

there was a code change for the 2002 NEC to clarify the disconnect means must be installed vertically unless impractical, then horizontal is ok. At an IAEI meeting, a CMP member explained the orginal meaning of horizontal meant mounted on the ceiling (from the 1920's), and not how we visualize it today.

Its perhaps not prohibited, but I would check with your AHJ. On a ceiling is not where I would look for a disconnecting means.
 