Greg1707
Senior Member
- Location
- Alexandria, VA
- Occupation
- Business owner Electrical contractor
Recently I encountered an unfamiliar situation. I was called to look at the panel in a townhouse/condo community. The townhouses had been converted to condos in the mid 1970s. There are about 4,000 units in the project.
The panel was a 150 amp panel with no main shut off. The neutrals and grounds were connected together. The water piping system was bonded to the panel. The panel was supplied by an underground cable with only 3 conductors.
Outside in the alley, fifty feet or more in distance, was a bank of meters. The meters were grouped in stacks of 3s. I removed the cover of the meter column and found there was no main disconnect nor OCP. There was a ground rod inside the meter housing.
Back inside the house at the panel I found the bus burnt on the breaker serving the electric furnace. I may need to replace the panel.
I am confused as to whether I can simply replace the panel with the current setup. Would not one expect OCP and main shutoff outside at the meter? Is the panel as setup now a service panel or a sub panel?
Is this installation up to modern standards?
The panel was a 150 amp panel with no main shut off. The neutrals and grounds were connected together. The water piping system was bonded to the panel. The panel was supplied by an underground cable with only 3 conductors.
Outside in the alley, fifty feet or more in distance, was a bank of meters. The meters were grouped in stacks of 3s. I removed the cover of the meter column and found there was no main disconnect nor OCP. There was a ground rod inside the meter housing.
Back inside the house at the panel I found the bus burnt on the breaker serving the electric furnace. I may need to replace the panel.
I am confused as to whether I can simply replace the panel with the current setup. Would not one expect OCP and main shutoff outside at the meter? Is the panel as setup now a service panel or a sub panel?
Is this installation up to modern standards?