4-140 Log #3389 NEC-P04
_______________________________________________________________________________________________
Donald A. Ganiere, Ottawa, IL
Add new text to read as follows:
Enclosures that contain the service overcurrent protective device and feeder or branch circuit overcurrent protective devices shall be provided with a barrier that isolates the service conductors and the service overcurrent protective device from the feeder or branch circuit protective devices. With the current design of service equipment that contain branch circuit or feeder overcurrent protective device, it is not possible safely install new conductors or circuits. The electrical safe work rules in OSHA and NFPA 70E prohibit working, other than troubleshooting, in these enclosures if the line side of the service overcurrent protective device is energized. The only way to comply with the electrical safe work rules would be to have the utility disconnect the service conductors before you work in the panel. This is not practical and leads workers to ignore the
safe work rules. This code change will make it possible to work in the service equipment without having the utility disconnect the line side power, by removing the (unacceptable) exposure to the unprotected line side connections.
This requirement has been in place for Canadian service equipment for many years. There is no reason why we can?t have the same protection for the electrical workers here in the U.S.
Canadian Standards Association Standard C22.2 No. 29, Clause 7.4.1.2 states: "The main switch or circuit breaker shall be located in a separate section of the enclosure with a sheet-metal barrier or the equivalent, of the same thickness as the walls of the enclosure, having bushed holes or the equivalent, for the necessary wiring between compartments". The major manufacturers of switchboards and panelboards currently make products that are in compliance with the CSA Standard so it will not be a hardship on them to comply with this safety rule.