I have a rather unique installation where I would like input as to "service points".
I have an industrial facility supplied by a local utility at 12 kv. The metering is on the 12kv line as the OH conductors enter the facility.
By agreement, the power company installs and maintains the lines beyond the metering point. In some cases the power company installs the primary conductors to power company owned and maintained pad transformers.
In other case the transformers are owned by the facility and the power company lines terminate at a set of 12kv fuses ahead of transformers.
The situation I have encountered is addressing the various supply points as services or SDS units. They are in the process of adding some 4350 kva 12kv/575 kva facility owned transformers as well as some 2500 kva 12kv/480 power company pad transformers. All feeding various sections of the facility.
It would appear to me that the facility owned systems would be SDS whereas the POCO owned pads would be services.
The way the NEC approached 250.30 especially in light of '11 addition of 250.30(A)(2) presents a bit of a problem.
Input appreciated.
I have an industrial facility supplied by a local utility at 12 kv. The metering is on the 12kv line as the OH conductors enter the facility.
By agreement, the power company installs and maintains the lines beyond the metering point. In some cases the power company installs the primary conductors to power company owned and maintained pad transformers.
In other case the transformers are owned by the facility and the power company lines terminate at a set of 12kv fuses ahead of transformers.
The situation I have encountered is addressing the various supply points as services or SDS units. They are in the process of adding some 4350 kva 12kv/575 kva facility owned transformers as well as some 2500 kva 12kv/480 power company pad transformers. All feeding various sections of the facility.
It would appear to me that the facility owned systems would be SDS whereas the POCO owned pads would be services.
The way the NEC approached 250.30 especially in light of '11 addition of 250.30(A)(2) presents a bit of a problem.
Input appreciated.