Re: Service Pole Hieght
Sorry Wayne, I assume this is an NESC issue because of the ownership of the poles and wires. My assumption is that these are owned by the serving electric utility. This also depends on whether or not the NESC is adopted by your state into law or if the electric utilities can make their own standards. I can only give you what I recall from memory since my copy of the NESC is in the office.
1. The lowest part of the drip loop is 12 1/2 or 12 feet, depending whether it is open wire or cabled on a messenger (triplex). If the construction of the structure is such that 12 1/2 or 12 feet can not be obtained, that may be reduced by no more than 2 feet.
2 and 4. The pitch of the roof has nothing to do with the NESC requirements. The clearance over a roof is 3 feet unless it is accessible to pedestrian traffic. If the roof is accessible to pedestrian traffic, the clearances in item 1 of my answer apply.
3. If the drop is within 6 feet of the through the roof raceway, it has to clear the roof by 18". There are no other restrictions as to the distance it may be over the roof.
The rules in 230.24 apply where the customer (owner or the owner's EC is required to install the service drop).