service question

Status
Not open for further replies.

bmwnut

Member
Location
O-H-I-O
New 200 amp service. can i install a 200amp meter disconect combo unit on outside then a 200 amp main lug[no main] in the house?
 
Yes.
HoltBlueDot.jpg
 
It's allowed if you treat the conductors between the main and the MLO as a feeder which means separated grounded and grounding conductors.
 