Service Raceway Bonding

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I'm having a brain fart. I have 10-4" EMT's entering a 4000 amp service with bonding bushings. To bond the service raceways I would size each bonding jumper according to the conductors within each raceway (600 kcmil copper). If using a single bonding jumper for all ten raceways what size would it be? 600*10*12.5%=750????
 
I'm having a brain fart. I have 10-4" EMT's entering a 4000 amp service with bonding bushings. To bond the service raceways I would size each bonding jumper according to the conductors within each raceway (600 kcmil copper). If using a single bonding jumper for all ten raceways what size would it be? 600*10*12.5%=750????
I think that's correct. 750 kcm
 