B bcgill Member Location New Mexico Dec 15, 2004 #1 Does 230.7 (Conductors other than service conductors shall not be installed in the same service raceway or service cable.) apply to J or pull boxes Bob
Does 230.7 (Conductors other than service conductors shall not be installed in the same service raceway or service cable.) apply to J or pull boxes Bob
B bphgravity Senior Member Location Florida Dec 15, 2004 #2 Re: SERVICE RACEWAYS Yes, if they are on the line side of the service disconnect and contain the service entrance conductors.
Re: SERVICE RACEWAYS Yes, if they are on the line side of the service disconnect and contain the service entrance conductors.