Good Morning!
I have a question about service rated vs. non-service rated automatic transfer switches.
Here's the situation. Industrial site owns an existing 34.5kV fused switchgear lineup that will serve a new 3000kVA transformer (34.5kV-480V). The utility meter/demarcation point is before the existing MV switchgear.
This transformer will connect to a non-service rated ASCO 7000 ATS (which does not have a main breaker on the normal side of the ATS). The ATS then connects to the main breaker of the 480V switchboard.
My question is: Do I need a service entrance rated ATS between the transformer and the 480V switchboard main breaker? Isn't my 'service disconnecting means' the MV fused switch feeding the transformer?
Thanks in advance for your help.