Bonham Electric
Member
- Location
- Sacramento, Ca.
- Occupation
- Electrician
The existing Meter/panel combo is a 200Amp rated Crouse Hinds underground fed with No 200 Amp main. The panel was factory wired from the load side meter jaws, with 3/0 copper to main lugs, feeding a buss with provisions for two double pole breakers. Existing is a 100 Amp 2 pole, feeding the mian sub panel and the other breaker is a 60 Amp two pole, feeding the condenser. Factory bonding consists of a ground buss, where the main neutral from the utility lands in the Utility section. The buss extends horizontally across the Breaker side and is factory bolted to the enclosure with 4 lugs, where the (2) #4 grounds land ( 1 is cold water, the other is a Ufer). The only neutral is the #2 Awg that is in a #2-3 romex and feeds the sub panel. We connected the service rated ATS with 2"EMT conduit and a 2ft piece of steel flex. A ground bushing was installed in the ATS where the #4 Green stranded was attached to the bushing lay in lug and then to the ground buss in the ATS. The feeders consists of (4) #2/0 locomotive cables ( 2 for utility, and 2 for load).The generator is a 24KW and produces 100 Amps. We installed a #2 white from the Main ground/neutral buss in the meter panel to the neutral buss in the ATS. The inspector had my tech add a jumper in the ATS from the ground buss to the isolated neutral buss.
As mentioned- The existing service required that You turn two double pole breakers off to kill all power to the house. With the New configuration, there is now a 200 Amp Main in the ATS. The ATS is mechanically connected with steel EMT and Flex with all steel fittings and bonded with #4 thhn and this ground is to the same buss where the original grounding is terminated. We also have a #2 Neutral that connects to the original ( common buss) to the ATS isolated buss. The inspector writes, without siting any specific code section, He just says Article 250. He States-1) " Generator configuration has new transfer switch as first point of disconnect. Main bond needs to be achieved ." A.-new "Main"and all grounds/neutrals isolated @ all load side sub panels. and 2.) " Relocate GEC termination to transfer switch.
So upon this statement the inspector is now classifying the 4 space buss in the original main panel as a sub-panel. The complication lies n the main ground buss there being commonly bonded to the enclosure and the utility neutral lands there. I am asking if anyone has a "exception" code or can give me any arguments that I could bring forth to the Solano County Building Department in My defense. We are contemplating changing the Service rated ATS out with a non service rated unit that has no main and the two original breakers will be the point of disconnect. This will cost me and the Client won't have as good of a system, but I don't know of any alternatives because to replace the main bonding would cost me about $1500.00 I have a series of pictures that I can send to any emails that reply by PM.
As mentioned- The existing service required that You turn two double pole breakers off to kill all power to the house. With the New configuration, there is now a 200 Amp Main in the ATS. The ATS is mechanically connected with steel EMT and Flex with all steel fittings and bonded with #4 thhn and this ground is to the same buss where the original grounding is terminated. We also have a #2 Neutral that connects to the original ( common buss) to the ATS isolated buss. The inspector writes, without siting any specific code section, He just says Article 250. He States-1) " Generator configuration has new transfer switch as first point of disconnect. Main bond needs to be achieved ." A.-new "Main"and all grounds/neutrals isolated @ all load side sub panels. and 2.) " Relocate GEC termination to transfer switch.
So upon this statement the inspector is now classifying the 4 space buss in the original main panel as a sub-panel. The complication lies n the main ground buss there being commonly bonded to the enclosure and the utility neutral lands there. I am asking if anyone has a "exception" code or can give me any arguments that I could bring forth to the Solano County Building Department in My defense. We are contemplating changing the Service rated ATS out with a non service rated unit that has no main and the two original breakers will be the point of disconnect. This will cost me and the Client won't have as good of a system, but I don't know of any alternatives because to replace the main bonding would cost me about $1500.00 I have a series of pictures that I can send to any emails that reply by PM.