Hey guys, I seem to recall that is not code to nipple a service rated transfer switch to the meter can, and feed the load side through the meter can.

Can anyone confirm this. I cant seem tofind it in my code book.

Howard
 
If you route the line side of the TS and the load side thru the same nipple it's a violation of 230.7
(Service conductors sharing a raceway with non service)
 