On a greenfield construction project we have a HVAC vendor who is proposing to install a service receptacle inside the RTU control panel. These are fairly large RTU's (FLA 60A, 480V)
210.63 requires that the service receptacle not be connected to the load side of the disconnecting means. My question - if we power the service receptacle from a separate 120V circuit, does it violate the requirements for disconnecting means. As proposed, the disconnect can be opened and locked out and there would still be live wires (the receptacle, powered by a separate 120V supply) inside the control panel. It seems counter intuitive to allow it but my manager is insisting it's fine.
ps. First post, please be nice!
210.63 requires that the service receptacle not be connected to the load side of the disconnecting means. My question - if we power the service receptacle from a separate 120V circuit, does it violate the requirements for disconnecting means. As proposed, the disconnect can be opened and locked out and there would still be live wires (the receptacle, powered by a separate 120V supply) inside the control panel. It seems counter intuitive to allow it but my manager is insisting it's fine.