Stevenwetzel94
- Hudson, FL
- Instructor
If an Electric Service is relocated and/or upgraded, do the branch circuits require to be brought up to current code? Including the requirement for GFCI/AFCI?
Maybe @Dennis Alwon can answer this as he is the one that wrote/requested the exemption for AFCI on panel changes. I don't know if it apples to the 2014 or not. Basically it says that if you have to extend the circuit wiring to reach the new panel, if it's not more than 6' you don't have to add AFCI.2014 NEC, could you point me to which article I could reference?
(B) Branch Circuit Extensions or Modifications —
Dwelling Units. In any of the areas specified in 210.12(A),
where branch-circuit wiring is modified, replaced, or extended,
the branch circuit shall be protected by one of the
following:
(1) A listed combination-type AFCI located at the origin of
the branch circuit
(2) A listed outlet branch-circuit type AFCI located at the
first receptacle outlet of the existing branch circuit
Exception: AFCI protection shall not be required where
the extension of the existing conductors is not more than
1.8 m (6 ft) and does not include any additional outlets or
devices.
"Ooh! Ooh! Pick me! Pick me!"I have my hand raised because I can actually answer this one.
Depends on your local AHJ.
Authority Having Jurisdiction. Means the (permits and) inspections department in your locality.Thanks for replying and giving your input! What exactly does AHJ mean? Thanks again.
Almost every municipality in my area requires smokes up to snuff with any permitted workI have my hand raised because I can actually answer this one.
Depends on your local AHJ. Call them and see if this a requirement. They may even want hard wired smoke detectors. Just by crossing the road into a different jurisdiction the rules can change.
