bthouse
Member
- Location
- St. Louis, MO
I am needing assistance with grounding/bonding a service. A house is being fed by 2 services, 400amp and 600amp single phase. (local utility will not allow single 1000amp residential service.) The CT cabinets, service disconnects, and ats' are remotely located from house. Each service is backed up by a generator. 100kw & 150kw with 3 pole ats ( neutral is being switched so it's considered a seperatly derived system.) The 2 services enter the house in the mechanical room and feed five 200amp panels. Now, do I have to run the water pipe ground out to the remote service disconnects and then back in with the panel feeders? Or, can I mount an insulated 1/4" thick copper grounding bus( article 250.64 C-3 ) in the mechanical room, run all the grounds to the busbar, and just bond the ground and neutral in the service disconnect? Hope all of that was clear.